Siemens S7 PLC+labview 7.0


Mize

Recommended Posts

...

I think I need OPC server/client software but would anybody have more specific information about the subject?

Mize,

You've got a lot of options and aren't necessarily limited to using OPC. A lot may depend on how many euros you have to spend.

A web search (example here) will bring up dozens of OPC servers for Siemens S7 and there are quite a few that make use of the "HMI Adapter" cable

Link to comment
  • 1 month later...

First of all, thank you dswaine for you reply. It provided help.

Since my first post things have evolved to a point where I can give simple boolean orders to the PLC, which then inserts pre-defined attributes to the ACH550-01 motor/frequency converter. The motor runs and there is a OPC server opening the PLC registry to LabVIEW via datasocket connection.

Now I am in a need of advice on how to write hex-values in labVIEW to let say address: PQW 258. I think I need something like slider which converts the values from 0-100 % to 0-4000hex and then writes this value to OPC-address. Would anyone have an example on how to do this?

-Mize

Link to comment
  • 1 month later...

Hello all,

I thought to drop back to report about my success. It was pretty hard to find information about the subject

but with a lot of patience and different approaches I managed to get the damn thing working.

What I used was software toolbox TOP opc-server to open the PLC registry to labview and then it was more

about creating the actual logic program with STEPS7. Used SFC14 ja SFC15-functions and data blocks to bypass

the 4 byte continuous limitation of PLC.

It has been a steep learning curve but I have enjoyed programming with labVIEW.

-Mize

Link to comment
Hello all,

I thought to drop back to report about my success. It was pretty hard to find information about the subject

but with a lot of patience and different approaches I managed to get the damn thing working.

What I used was software toolbox TOP opc-server to open the PLC registry to labview and then it was more

about creating the actual logic program with STEPS7. Used SFC14 ja SFC15-functions and data blocks to bypass

the 4 byte continuous limitation of PLC.

It has been a steep learning curve but I have enjoyed programming with labVIEW.

-Mize

Hello Mize

In my industry, at first we "solved" this problem problem by installing Step7(or Wincc and just declare every tag on a dummy project) on the same computer as labview, or RSLinx if the PLC is Allen Bradley. In every case we need a license from Siemens or AB, something that was out of question, especially for Siemens, because they are TOO expensive, even for a single license. Then we found out about IBHSoftec, which besides the OPC server provides some nice tools and cables, AND S5 for Windows.

Hope i helped.

Link to comment

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.