Hello,

I am using NI's Modbus Library and am having a problem. I am trying to read data at Modbus address 404198. However the address input is 16 bit and can only accept a maximum number of 65535.

Any sugestion?

post-8614-1213975922.gif?width=400

Posted

404198 is really address 4198 of the holding registers. 4 = holding registers.

Most Modbus servers are one based so 400001 is this first holding register (offset 0).

In your picture you going to read 365535 because your trying to read input registers, 3 = input registers.