Change from Fieldpoint to CompactDAQ AI gives strange values


Recommended Posts

Dear all

We got a strange problem when moving from a Fieldpoint with a FP-AI-110 to CompactDaq rack with a 9203 (and also a AO, DO, DI module to in additon to the 9203, we used a 6009 before), there is one pressure sensor 4-20mA and one temperature sensor 4-20mA.

Before the change the readings were normal now they have very high noise overlaid, resulting in a pressure from -2 to 3 bar when unpressurized.

We have tried about 10 different ideas to eliminate the problem but with no success yet.

Any ideasor suggestions are highly appreciated !

Best regards

Anders

Link to comment

Never used those modules before, but have you tried grounding any unused channels?

Also, are you getting 4ma when the pressure is 0? I've never had a pressure sensor give exactly 0 output when the input is 0 pressure. You might want to scale the values before presenting the output.

Neville.