I am assigned to refurbish an airflow instrument having six pressure sensors, four temp sensors, and six on/off outputs. By preference I would use all NI hardware, but this isn't going to be allowed. I'm being pushed toward installing an Allen Bradley PLC instead. I am aware of another, much more complicated liquid flow test stand which, so I'm informed, uses LabVIEW for SCADA on a Seimens PLC. This being the case, cannot I do likewise with Allen Bradley? Can I do it entirely in LabVIEW? Or is something like that always just LabVIEW sending trigger commands and receiving data from a free-standing program written in the PLC's own native SCADA?

I'll be starting from scratch, with nothing yet purchased. I can purchase whatever I choose. I have perused a couple of PDFs of Allen Bradley ControlLogix programs, and at first glance, to me they look like a major pain. Unlike LabVIEW, almost nothing shows on any one screen. Nothing at all looked to have been nested into a subroutine. I liked ladder and highway diagrams quite well enough back in the 90's when printed out on D-size vellum. Then, at least, I could stand back and see the whole thing. The same thing seen only through a tiny window that you have to scroll up and down I'm not looking forward to learning at all. Thus my hope for a LabVIEW solution, rather than purchase and learn AB's Studio 5000. I'm an old dog, and this looks like a new trick to me.

Edited by Gan Uesli Starling
double word

Share this post


Link to post
Share on other sites

I'm throwing in my all the way incomplete point of view, because my current project is a SCADA too, and I decided to go the labview way. However, I'm still asking myself about the rationale of my decision, and about the option of integrating PLCs at a later stage. At the design phase I looked at some docs of a few PLC vendors and their control software, and was scared off by their license tems (LV we have academic), by the learning curve and by the apparent (to me) clunkiness. Add to that that I presume that the bonanza I can get from the LV community largely surpasses the support, even paid, which I could get from a solid SCADA vendor.

It seems you are still deciding whether you need PLCs or not. If you're excluding NI (realtime standalone?) hardware, does it mean that you can afford the increased instability risk of running your business logic on a desktop computer? Is safety among your requirements?

(No connection with the particular vendor), I ended up purchasing a number of these Advantech ADAM-5000 modules, which seems a decent compromise for my needs. On one side, they are ruggetized and modular remote IOs, which I can easily read as modbus registers. On another, they seem to have a minimal capacity for an embedded logic (e.g. you can define logic functions of three inputs which are routed to another register of the same or of another module), thus potentially overlapping with minimal PLC capabilities. I'm currently testing them. Has anyone else used them and would share opinions?

Share this post


Link to post
Share on other sites

It's a political thing. In my own department (Test Engineering) we are fully invested with LabVIEW. The test stand in question, however, belongs to another department. And they are devoutly enamored of Allen Bradley. Cost is no issue, my company has full, all-encompassing corporate licenses for both NI and AB softwares. I am considered something of the plant-wide hardware and software guru, if only because I've been here 12 years. But this project got handed to me already with the AB constraint. Bit of an uphill slog in my future, so it would seem: new hardware & a new authoring platform.

Share this post


Link to post
Share on other sites

In general I am however interested in hearing about experiences and opinions about LV vs. X for building SCADAs. A quite broad question I understand, and much dependent on plant size and boundary requirements, but still.

In my case some of the arguments which drove me once more to LV were: heterogeneity of the hardware to be controlled, need to interface with other systems, perception of a higher freedom and power in concocting the HMI, academic rather than industrial work culture, presumption of insurmountable learning curves and additional license costs.

Share this post


Link to post
Share on other sites

Might be a case for a AB Micrologix.  These interface nicely with LabVIEW. 

Last time I used one, it was still good old ladders.  :) 

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.


  • Similar Content

    • By Abel_Souza
      LabVIEW 2016
      Modbus Communication with a PLC Siemens SIMATIC ET 200SP
      Windows 7 Ultimate
       
      Hi,
       
      When I run my code it return error 66 at Read Holding Registers function. I ran this code as a VI on the development virtual machine and as a *.exe on real machine, but received the same error.
      Try in another computer and receive the same error.
      As PLC code was developer by other programmer I ask him if this communication was working on his machine, he showed me a LAbVIEW code running with Modbus communication with the same PLC. He was using a LabVIEW 2013 with old Modbus Library, but I had taken his code and ran on my PC with LV 2016 and receive the same error on MB Ethernet MAster Query Read Holding Registers(Poly).vi. Also generate an exe file and run on my real machine and still receiving error 66.
      In all scenarios I can ping PLC and receive answers, but cannot read or write any data with LabVIEW.
       
      First picture is my code with LV 2016 VIs.
      Second picture is error message.
      Third one is the other programmer code with old Modbus Library.
       

       
      On the first code, if I remove Read Holding Registers VI and connct wires directly or put a property node to set any property it runs without errors. If change this function for any other modbus function return error 66.
       
      Any idea what I am doing wrong?
       
      Thanks in advance!
      ni_support.zip
      Comunicação CLP.vi
      Main_MB_2.vi
    • By dterry
      Hello all,
      I recently was presented with the task of integrating a Mitsubishi PLC into our systems. After a good deal of googling, I think the best (maybe only) way to get the data out is going to be via OPC, thanks to their proprietary Melsoft protocol. If anyone else knows a better way, feel free to stop me here.
      Now, we are currently expanding our data generating capabilities (hence the PLC), and I have been thinking about rearchitecting the way we collect data from all over our facility to be more flexible.  Since I may be required to use OPC anyways, I was considering using an OPC server to aggregate all of the facility data, and then redistribute to control rooms, historical logging, etc.  To do this, we would need to integrate our cRIOs and operator PCs into the OPC environment as well.
      I don’t see OPC mentioned very often (in fact it returns 0 results on LAVAG), and a lot of the stuff I see these days seems to be more “roll your own” or lower level (raw TCP/UDP, 0MQ, Network Streams, Transport.lvlib etc.) rather than a monolithic abstracting bridge like OPC. Unfortunately, I won’t have time to roll my own in the near future, but LVRT supports supports OPC UA, so I could potentially integrate the cRIOs fairly easily.  Unfortunately, I think I would have to use LabVIEW DSC (or datasockets...) to integrate the PCs.
      I would be very grateful if anyone has the experience to comment on the following or anything else related to using OPC.
      What are viable update rates for OPC tags?  I will need at the very (very) least 250 ms update rates.  Is OPC typically low latency (time from data generated to to client received)? Does anyone have a recommendation for a product (NI OPC, Kepware, etc.)? Is OPC still popular, or are there other options for data aggregation that would be better suited to a new application? What are the options for logging and alarming with OPC? What are the options for talking to OPC from LabVIEW? How robust are the OPC connections in regards to reconnecting if a wireless connection is temporarily lost? Thanks in advance!
    • By Ricardo de Abreu
      Hi Guys, I'm with a trouble here.
       
      Recently we started to get our outdated temperature test cabinet to work, and the best way is to upgrade our PLC. But there cames 2 problems, the biggest is the budget, we do not have any money so we have to work with what we already have, and the second, i'm intern here and there is no one from automation to guide or help me.
       
      Now lets face the problem.
       
      PLC Allen Bradley micrologix 1100
      cards: 1762-IQ16 and 1762-IQ8W6
       
      My first thought is to use Labview to control the PLC, as HMI and data-logger without OPC server to simplify the instalation and cost.
       
      The communication: this is really where the problems begin. It will be done through Ethernet. I could not manage Ethernet/IP driver to work, nor pcc or CIP message...
       
      which is the best way to communicate?
      CIP Message, OPC, or any other i do not know? Do you guys see any problems to make a dataloger without OPC?
       
      Some things I have tryed
       
      Implementation of Common industrial Protocol (CIP) via EtherNet [EtherNet/IP (CIP)]
      https://lavag.org/topic/6104-industrial-ethernet-ethernetip/?page=1
       
      Ethernet/IP Driver for Micrologix 1100
      https://decibel.ni.com/content/docs/DOC-13024
       
      EtherNet/IP Driver for Industrial Communication
      https://decibel.ni.com/content/docs/DOC-4065
       
       
      Thanks for any help
      Ricardo
      PS. Originally posted at: https://decibel.ni.com/content/thread/47497
    • By Ricardo de Abreu
      Hi Guys, I'm with a trouble here.
       
      Recently we started to get our outdated temperature test cabinet to work, and the best way is to upgrade our PLC. But there cames 2 problems, the biggest is the budget, we do not have any money so we have to work with what we already have, and the second, i'm intern here and there is no one from automation to guide or help me.
       
      Now lets face the problem.
       
      PLC Allen Bradley micrologix 1100
      cards: 1762-IQ16 and 1762-IQ8W6
       
      My first thought is to use Labview to control the PLC, as HMI and data-logger without OPC server to simplify the instalation and cost.
       
      The communication: this is really where the problems begin. It will be done through Ethernet. I could not manage Ethernet/IP driver to work, nor pcc or CIP message...
       
      which is the best way to communicate?
      CIP Message, OPC, or any other i do not know? Do you guys see any problems to make a dataloger without OPC?
       
      Some things I have tryed
       
      Implementation of Common industrial Protocol (CIP) via EtherNet [EtherNet/IP (CIP)]
      https://lavag.org/topic/6104-industrial-ethernet-ethernetip/?page=1
       
      Ethernet/IP Driver for Micrologix 1100
      https://decibel.ni.com/content/docs/DOC-13024
       
      EtherNet/IP Driver for Industrial Communication
      https://decibel.ni.com/content/docs/DOC-4065
       
       
      Thanks for any help
      Ricardo
      PS. Originally posted at: https://decibel.ni.com/content/thread/47497
    • By FJ_Sanchez
      Hello,
       
      I've been using Snap7 library for a while in the client role, so I can communicate with SIEMENS PLCs There is specific LabVIEW info here: http://snap7.sourceforge.net/labview.html
      I can successfully use the Cli VIs to read/write from PLCs DBs (a DB is just a memory block). For reading I pre-allocate a buffer, but I'm not sure if I'm doing it properly. My main concern is about memory leakage, I don't know if the memory will be freed after the VI exits or it will not be freed as long as the VI is in memory.
       
      Attached is what I have just now for reading. I define a typedef for each DB, it is a cluster of booleans, and reserve memory according to the number of booleans, but always in multiple of 8 (I read only bytes). I request the data with the CliDBRead and after that I make some conversions to return the data in a variant that I later cast to the proper typedef.
       
      Can you tell me if this is the best way to do this?
       
      Thank you!

×
×